- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
He would have to accept as the EVSE is not an appliance. Also, it has a separate code section that covers only EVSE.AHJ may or may not accept
He would have to accept as the EVSE is not an appliance. Also, it has a separate code section that covers only EVSE.AHJ may or may not accept
But he tendency to tag citing 422.31(B)He would have to accept as the EVSE is not an appliance. Also, it has a separate code section that covers only EVSE.
What part of this is not an appliance do you not understand?But he tendency to tag citing 422.31(B)
Lockable Disconnect Requirement for EVSE Under 60A/150V?
Hi all, I’ve been encountering some differing interpretations from local inspectors regarding when a lockable disconnect is required for EVSE installations. Specifically, this concerns EVSE rated at 60 amps or less and less than 150 volts to ground. My understanding has been based on NEC...forums.mikeholt.com