48A tesla charger

He would have to accept as the EVSE is not an appliance. Also, it has a separate code section that covers only EVSE.
But he tendency to tag citing 422.31(B)
 
But he tendency to tag citing 422.31(B)
What part of this is not an appliance do you not understand?
 
Even if the AHJ insists on applying 422 (which I agree they should not), those requirements can be complied with using a breaker padlock device in the panel, at most. There's no requirement for an additonal disconnect at the appliance.
 