- Tennessee NEC:2017
- Semi-Retired Electrician
No inspector would have even seen behind the new panel. I would have it up before calling for inspection.
What if he has a checklist?No inspector would have even seen behind the new panel. I would have it up before calling for inspection.
Since there is by design a 1/4 in airsapce behind the panel the NM connectors above the busbar would get me flagged here, but we get pretty wet winters here.Whether a panel listed for surface mount can be installed as a recessed panel not sure of listing limitations but the 2023 NEC states:
"312.2 Damp or Wet Locations.
In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm (1⁄4-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations."
You don't get it. If the panel is sealed to the wall the back is no longer a wet location. If you inspectors still feel it a wet location they should be more worried about the in in the building than the NM cable.Those meter / loadcenter center's have little dimples in the mounting holes to push it 1/4" off a flat wall for the required airspace. From the photos its not 100% clear if the meter / loadcenter center is truly surface mount, as in 1/4 in off the with the airspace? But it also does not seem semi flue / framed in so I'd have to agree with Fred;
As @AC\DC DC suggests you can semi recess a panel like that,
I just did one here with the help of a carpenter the inspector requires the 'vapor barrier to be restored' the hole gets flashed and trimmed like a window, the carpenter used that tape they use around windows, definitely more than caulk involved.
Even then all the NM enters below the busbar, and each NM is secured to the panel.
In this case I'd probably have pulled upper those NM into a jbox and ran a exterior raceway into the panel.
Does a surface mount panel not require airspace? If that panel were sealed flat to the wall how would it comply with 312.2?You don't get it. If the panel is sealed to the wall the back is no longer a wet location.
312.2 does not apply to a bell box. For AC disconnects your not typically entering above live parts.I take it you have never installed a surface mount A/C disconnect or "Bell Box" with NM cable entering from the back?
OK do you typically see installs like the OP with raceways or cables above the level of uninsulated live parts with dry location fittings?The panel is mounted with the dimples. If the edges are sealed on the top and sides with the bottom open then the air space still exists.
If it's entering from a dry location then yes.OK do you typically see installs like the OP with raceways or cables above the level of uninsulated live parts with dry location fittings?
No.If you seal the edges on the top and sides with the bottom open, still outside the building envelope, is that 'air gap' considered a dry location by the AHJ's in your area?
Yes if it was completely enclosed it would no longer meet the definition of a wet location.Guys
I always try to think outside the box
Can you build a closet around the panel
Are we out of a wet location now?