Raceway Bond to EGC

Need a little clarification for bonding jumper.... Our contractor ran a 4/0 bare ground from equipment to a plate which ties into the grounding grid. Since this was done in EMT they installed a #6 bonding jumper from the conduit to the plate as well. Our client has concern that this jumper will not provide sufficient protection if someone were around the conduit and a fault would occur. I can't find anywhere in the code concerning a bonding jumper for the raceway when bonding an EGC specifically, only thing I found deals with bonding conductors and equipment... I feel that #6 would be fine, but just want to be sure that workers are protected. Thoughts?Bonding Jumper.png
 
Are those #4/0 conductors GEC's? If so the#6 also needs to be #4/0. Also GEC's play a very little roll in fault clearing.
 
I agree with Rob, those appear to be GEC's and bonding to both ends are not actually for personnel safety. With that said they should have used a fitting similar to below and they wouldn't need the bonding jumper. They are made in other materials than brass.

1761310792560.png
 
As Roger suggested grounding hub on the end of the raceway is the easiest method as it avoids the need for #4/0 going through a bonding bushing.
 
My understanding of GECs is they have to go directly to earth/ground per 250.53 and even if a supplemental plate were used the bonding jumper wouldn't have to be larger than a #6 per 250.33 (E). The current set up simply looks like an equipment ground to the plate/grounding grid, not a GEC, but an EGC.
 
My understanding of GECs is they have to go directly to earth/ground per 250.53 and even if a supplemental plate were used the bonding jumper wouldn't have to be larger than a #6 per 250.33 (E). The current set up simply looks like an equipment ground to the plate/grounding grid, not a GEC, but an EGC.
A GEC is earthed but not necessarily jumpers so tell us where the conductors land on the other end. If they are intended to be EGC's you have a problem with 300.3(B)
 
Sounds like someone is making an effort to meet 250.54 and if that is in fact the case it's not much of a concern except for added expense to the project.
 
Well regardless, since there is an EGC run with the circuit conductors these are mostly a waste of materials and labor
Since the EGC is run with the circuit conductors and these are just additional bonding jumpers that are not required by any code then I don't see a requirements to run them in any certain way.
 
My understanding of GECs is they have to go directly to earth/ground per 250.53 and even if a supplemental plate were used the bonding jumper wouldn't have to be larger than a #6 per 250.33 (E). The current set up simply looks like an equipment ground to the plate/grounding grid, not a GEC, but an EGC.
EGCs have to run with the circuit conductors. They are not permitted to be run by themselves.
These appear to be GEC,s and where run in a ferrous raceway a full size bonding jumper between the GEC and the ferrous raceway is required by 250.64(E).
 