NEC 210.8(B) All 125V through 250V receptacles supplied by single phase branch circuit rated 150V or less to ground, 50A or less, and all receptacles supplied by three phase branch circuit rated 150V or less to ground, 100A or less, installed in kitchens shall be provided with GFCI protection.
We ran into an elec. inspector, per his code interpretation and he considers "receptacle" will applies to all equipment in kitchen has hardwired connection as well, do you agree? I looked at receptacle definition and not sure this convinces me unless the latest NEC code changed.