g-and-h_electric
- northern illinois
- supervising electrician
Let me start with, the manufacturers instruction arent clear!
So we have a newly installed air handler with a total of 15kW of electric heat strips in it. They are factory split 2 stages, with stage 1 is 10kW, and stage 2 is 5kW. Onstage 1 is the control transformer, and the blower of about 3 amps.
The unit came with 2 circuit breakers ( yes I checked they truly are breakers not just disconnects. Stage 1 is a 60, and stage 2 is the same. MOCP is 60 for stage 1, and 25 for stage 2. Obviously without swapping the stage 2 breaker I cannot use the "tap rule" to feed both stages from a 125 amp feeder. the main breaker panel is in the same room as the air handler and within sight. Anyone have a problem with removing the existing #1 THW conductors, and replacing them with 2 #6 (on the 60), and 2 #10 (on the 25) with the breakers in the main panel, and the air handler labeled to indicate that there are multiple branch circuits feeding it and which circuits they are?
Howard
Howard