1” emt to a 4 square
Pinnie
Ohio
Commercial Electrician
In the company I work for, guys will knockout or drill out a hole for a 1” emt into a four square. I think even as a pull box you would be over on a full boat 10 AWG pull, but what is the legality of such a modification?
You can punch or drill it for a 1 3/8" hole if needed. The box fill doesn't change based on the raceway entry size. Regarding the #10's a standard depth 1900 box allows 6 and 2 1/8" deep allows 8.
If you pulling 10 AWGs 3/4 accomplishes as many circuits as 1” so those 4 squares would serve only the purpose of pulling larger wire.
Where in NEC do we learn limits of modifications?
The NEC doesn't cover a specifics of modifications. It really comes down just to 110.3 and what is acceptable to the AHJ. I have a hard time seeing punching a hole or enlarging a hole in a box as being unacceptable. Unfortunately though, there's a large movement in the inspector/AHJ community to demote electricians to installers and not allow them to make any decisions or make any necessary field modifications. Why they trust the listing people so much after all their failures is beyond me.
Not sure I understand what limits of modifications means. Boxes can be punched, many come with no holes in them at all. You can always installed an extension box to increase the number of conductors allowed.
I guess I’m wondering what we are “supposed” to do. Lookup to ul listing on each box/enclosure and see if they allow us to punch holes in boxes that have predetermined knockouts?
I’ve seen 1.5” rigid into a 4sqaure box. Crazy looking barely any metal left after they punched it.
Thermostat wiring with tray cable. Why on earth the company chose that idk
I did this recently and used 4 sq's with 1" KOs. ITs just a full boat of #12's in one and a couple cat6 in the other, I just like to use 1" for these drops b/c 3/4 seems a little flimsy.
Depot started spec’ing 1” drops a few years back on new stores, don’t know if they still do. Quite a bit more expensive than 1/2” with that many drops. Not much is going to hold up to a misplaced pallet though! LOL!
Although it looks good and I have no issue with it, isn't there a violation of 300.11(C) Raceways Used as Means of Support?
Mark