Two pool related questions

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
1. The pool I’m wiring is within 5’ of the single family house with aluminum siding. I assume I would have to bond the siding with a #8. What would be the best way to do this, or what type of lug?

2. On the pool pump it doesn’t state the horsepower. How can I figure it out? The homeowner wants a 240v double pole switch installed for the motor.
 

Attachments

  • IMG_2713.jpeg
    IMG_2713.jpeg
    339.2 KB · Views: 11
  • IMG_2714.jpeg
    IMG_2714.jpeg
    427.7 KB · Views: 11
What about a lug, any idea what you would use? I never dealt with bonding aluminum siding
There is no electrical connection between the individual pieces of aluminum siding, and there is no way to make a 250.8 compliant connection to aluminum siding without popping each section off, and using a lug, screw, and nut.

This picture shows typical aluminum siding with the ungrounded conductor connected to one section and the EGC connected to the next section. There is no continuity between the two sections of siding.
1762101974487.jpeg
 
It's a problem. The pool should be more than 5' from the house. I had a guy who set a hot tub on his patio. The supports that held up the patio roof were metal and there were two of them within 5'. When I questioned him he said "the sauna guy said it was ok"

I bonded the supports with #8 and his wife took a fit said it "looked ugly"
 
He just showed you that unless you bonded every single piece of siding, bonding would do no good. IMO, bonding one section would be more dangerous than no bonding. I would not bond it.
That’s what I was wondering, if it should be bonded or not. How would you address this with the inspector? State I think it’s more of a hazard if I bond in one spot?
 
Last edited:
That’s what I was wondering, if it should be bonded or not. How would you address this with the inspector? State I think it’s more of a hazard if I bond in one spot?
If he uses a little common sense he should see it can't be bonded unless each section is bonded. If I were doing this, I wouldn't bond it, nor mention anything to the inspector unless he brought it up. Then I would explain to him why not to bond.
 
This is insanity. Grounding the siding? What then next? Grounding the car in the driveway? the rebar in the concrete? then don't forget the staples used on Romex in the house. Need to bond all of them together. Don't forget the metal mail box by the driveway. Need #12 THHN run to that. Green. Make sure it's labeled. Land a ground rod at the mailbox too. ???
 
You may want to refer to 680.26(B)(7). I bet a lawyer will. Inspections shouldn’t be an Easter egg hunt.
 
How would you suggest to bond the siding?
A method provided by 250.8(1)-(8)? I think you guys have already come up with the answer but decided it was too labor intense or would be an eyesore. The pool shouldn’t have been constructed within 5’ of fixed metal parts if someone isn’t able to come up with code compliance to 680.26(B)(7). Isn’t it really as simple as that? Just because it is hard to do is not an excuse for non compliance.
 
A method provided by 250.8(1)-(8)? I think you guys have already come up with the answer but decided it was too labor intense or would be an eyesore. The pool shouldn’t have been constructed within 5’ of fixed metal parts if someone isn’t able to come up with code compliance to 680.26(B)(7). Isn’t it really as simple as that? Just because it is hard to do is not an excuse for non compliance.
There is ZERO hazard in not bonding it. I would not require it to be bonded if I was inspecting.
 