- Location
- Wisconsin
- Occupation
- PE (Retired) - Power Systems
It is wild because it is higher than 120V.It's just the way the transformers are wired. The wild leg is called "wild" because of the wild voltage variations. I've seen 135v, 165v, 189v and 200v in the same day (hot to neutral). POCOs told me it's normal based on the building load, and grid load both.
Per the NEC and ANSI standards the nominal voltage would be a 240/120V delta. By the laws of physics the high leg is always1.732X the center tapped L-G voltage.
Any deviations are due to voltage drop at the load or under voltage supplied by the utility. In both cases this would also impact the nominal 120V L-N and 240 L-L voltages.