I have a 800A line side tap fused disconnect on a 1600a 3p 480v service. My line side conductors are 3 parallel runs of 400kcmil aluminum with a 4/0 aluminum GEC. I have bonding bushings on 3” EMT on both sides coming from the fused disconnect into the tap section of the switch gear ahead of the building main disconnect.
My question is: I believe I have to wrangle the GEC through the bonding bushings on both sides, which with 4/0 is going to be pretty challenging. I’d rather use a bonding jumper, but my interpretation of 250.102(C)(1) is that the bonding jumper to the bonding bushings would still need to be 4/0 because my ungrounded conductors are 400’s x 3 = 4/0 because that lands between 900 and 1750 in the aluminum column.
Am I seeing that right? All of my 3” bonding bushings max out at 1/0 with the lay in lug included, so I’ll need to order lay in lugs that can even handle 4/0.
My question is: I believe I have to wrangle the GEC through the bonding bushings on both sides, which with 4/0 is going to be pretty challenging. I’d rather use a bonding jumper, but my interpretation of 250.102(C)(1) is that the bonding jumper to the bonding bushings would still need to be 4/0 because my ungrounded conductors are 400’s x 3 = 4/0 because that lands between 900 and 1750 in the aluminum column.
Am I seeing that right? All of my 3” bonding bushings max out at 1/0 with the lay in lug included, so I’ll need to order lay in lugs that can even handle 4/0.