It sounds like it would be manually started. In that case they can be permitted to manually manage their own loads manually since they already are aware they are on generator. 702.4(A)(1)

Standalone generator would feed service switchboard that has essential branch. My question is about generator sizing. See previous post


Sent from my iPhone using Tapatalk
 
In my area the max kW is on every bill. Under "actual demand", as well as kVAR, kVA etc. If it's not on the bill, I can assure they have the data. How could they bill demand charges if they didn't ?
That is my thinking. If you are being charged a demand charge, then that maximum value will be on the bill. There are certainly different commercial rate structures where you might not be billed for demand, so then I could see not having it. In my experience the vast majority of commercial accounts are billed demand however.
 
I get billed T & D charges based on max demand with a 15 min duration. So if I draw 100KW for 10 minutes and 50KW for 16 minutes the next highest for the billing period, all I see on my billing is the 50KW charge.

So I guess you can see where using demand numbers can be a problem
 
That is my thinking. If you are being charged a demand charge, then that maximum value will be on the bill. There are certainly different commercial rate structures where you might not be billed for demand, so then I could see not having it. In my experience the vast majority of commercial accounts are billed demand however.

Utility here gives kwh only per month. See post #19. What do you think your opinion would be about question in post #19?


Sent from my iPhone using Tapatalk
 
I get billed T & D charges based on max demand with a 15 min duration. So if I draw 100KW for 10 minutes and 50KW for 16 minutes the next highest for the billing period, all I see on my billing is the 50KW charge.

So I guess you can see where using demand numbers can be a problem
The extra 25% should cover that. In fact I have logged both demand and max KW, and I find that 125% of max demand is usually pretty close to max KW.
 
Utility here gives kwh only per month. See post #19. What do you think your opinion would be about question in post #19?


Sent from my iPhone using Tapatalk
So you (or your client) are not billed for demand?

Yes you can measure for 30 days. What is the probelem? IT says you can measure for 30 days so why do you think you cannot?
 
So you (or your client) are not billed for demand?

Yes you can measure for 30 days. What is the probelem? IT says you can measure for 30 days so why do you think you cannot?

I thought minimum 30 days metering wouldn’t be allowed if I have hospital like setting with essential branch and to size standalone generator which serve basically as service until new service switchboard are replaced


Sent from my iPhone using Tapatalk
 
Be sure to consider kVA demand as well as kW demand. If you can get kVA data that will really tell you how to size and be ready for a big amp draw. (motors and compressors)
 