My boss used a estimating service to bid a 33 unit HOA to do some electrical upgrades I am looking it over on a Sunday before its due in. There is one odd thing to me, these 50A receptacles for EV's going in garages that call for a 6/2 cable, 50A breaker and a 14-50 receptacle. Apparently that is what some other EC's did recently in another section and it passes inspection.
You cant pigtail a EGC to the neutral pin I know the code says that,
but you can leave the neutral open is that correct ? Did this other EC somehow slip this by the inspection agency?
The way inspections work here we may get a different inspection agency than the one the approved the other section so even if we do what they want I doubt it will pass, and frankly it seems just wrong.
Before you all say it I already emailed them back and asked they do a RFI and see if NEMA 6-50's can be installed. I see there is 6-50 - 14-50 adapter on amazon for under $20 designed for EV's and some EVSE do come with a 6-50, offer one or allow you to choose. And honestly they may not even notice RFI or not so I'll probably just use 6-50's.
Do any of you install 14-50's with no neutral?