Back to back strut
Alwayslearningelec
NJ
Estimator
Not sure I've seen this much but why woild one use back to back strut for trapeze racks ..some with only 4 conduits. I understand added support but I believe I've seen conduit runs like this with just 1-5/8 strut .
The strut manufacturer publishes information on how much weigh the strut can support along with how close together the supports need to be etc.
If there is nothing run on the bottom strut the it's likely that they used back to back strut for physical strength.
I agree and if you end up with left over from another project you use it where it's not actually needed.
I assume it's more practical to buy it back to back then assemble....should it's welded together or something similar so assembling wouldn't even in be an option.
They also make strut deeper than the standard 1 5/8" tall strut. I think you can buy 3" deep strut and maybe 2 1/2" I forgot.
The back-to-back double 1 5/8" is riveted together, I think.
I would think no longer than it is a 1-5/8" strut would be sufficient. Size of suspending rods and what might they hanging from possibly can be more questionable than using 1-5/8" strut there?
As others mentioned it may be back to back assembly that is factory welded or riveted, though I think isn't necessary here.
I can't look at racks of strut and all thread without thinking about the the Hyatt Regency in KC. I know the applications are way different, but those stress flows. And to make matters worse people were dancing on it to a beat
Looks like 1/2" rod which can support thousands of pounds depending on the type of anchor used.
Right but what determines that? Some sort of calcs or judgement call? Barring spec requirements.
Lots of calcs, especially if there are seismic requirements. I don't see any diagonal bracing on those strut trapezes, so must not be a seismic area.
The back-to-back strut also give you some room for expansion if they happen to plan for that. We did lots of strut trapezes with cable try on top of the strut and conduits on the underside. Those were single channel though, with the channel facing down and the tray on the flat back of the strut.
Easy way to remember the depth of extra deep strut is to double the 1 5/8" deep strut. = 3 1/4" deep. Same with 13 /16" shallow strut ( double that = standard 1 5/8" deep strut. They do make a size between 1 5/8 & 3 1/4" strut but my two local supply house never stocked it. If we were installing 8 to 10' wide strut for larger conduits felt that back to back 1 5/8" strut bolted together was stronger by then a piece of 3 1/4" strut. Love unistrut so much that when I removed a few hundred feet from an old supermarket I used it to build shelves entire length of garage wall. Cut plywood into three pieces 32 by 48". Went 32" deep so a long & a short milk crate would fit back to back.
We’ve always called it JR(7/8”),
SR(1 5/8”), and grandpa strut at (3 1/4”)
On one big job that had over 30 3/4" conduits that all had a total of 360 degrees in bends from single & three phase panels I was able to mount deep 1900 boxes on 5/8" deep unistrut and came down the wall with 7/8" deep strut. That saved me from installing over 30 C condulets and not having to bend over 30 box offsets. Was for an injection molding plant that needed two 120 volt duplex receptacles, A 208 single & three phase 20 amp receptacle and a 480 volt 20 amp twist lock receptacle every 12 feet for each machine. Wish I had a dollar for every foot of strut I installed last 50 years.