jeffreylee7469
Member
- Location
- washington county, PA
- Occupation
- electrician
I was asked to look at this transformer. The transformer is being used as a step-up transformer, but I don't see any specs that state the transformer can be used this way. The wiring is 120/208v primary and stepping up to 240v secondary. The specs are labeled as 3-phase, corner grounded delta (primary) and 3-phase wye (secondary). The owner had the transformer wired so x1, x2, and x3 (secondary) were the primary and the H1, H2, H3 (primary coils) are the secondary feeding a 3-phase 240v panel. The 208v input is a 3-wire input without a neutral, so the x0 lug is not used. The EGC is bonded to the transformer chassis. The reading on the coils is 240v phase to phase (A-B/ B-C/ C-A). When reading to ground A-phase 240v to ground, C-phase 240v to ground. B-phase is 0v to ground.
The issue is the owner has a 3-phase oven that is on a 50 amp 3-pole breaker. The homerun to the oven lands on a 40-amp, 3-pole breaker in a control panel and this breaker feeds a 3-phase relay for the heating elements. When the oven is turned on, one phase is pulling up to 120A then the breaker trips in the control panel. Nothing else in the 240v panel is affected. Is this transformer capable of being used in this means? Is there a problem with the grounding? Does x0 need to be bonded with the EGC? Is this an oven issue?
The issue is the owner has a 3-phase oven that is on a 50 amp 3-pole breaker. The homerun to the oven lands on a 40-amp, 3-pole breaker in a control panel and this breaker feeds a 3-phase relay for the heating elements. When the oven is turned on, one phase is pulling up to 120A then the breaker trips in the control panel. Nothing else in the 240v panel is affected. Is this transformer capable of being used in this means? Is there a problem with the grounding? Does x0 need to be bonded with the EGC? Is this an oven issue?