So there is a high leg there. They are feeding the transformer with the 120/208Y. The in house guy is telling me that the voltage across the Delta used to be 120 per phase and 240 phase to phase. I measured 240 phase to phase and A /C phase measured 240 to ground. 0 volts on B to ground.
This is contradictory. Perhaps there used to be a high-leg (different transformer) and at some point it was converted to corner grounded. But a high-leg and a phase 0V to ground should be a dead short, not possible even if the transformer had a center tap for a high-leg (which the label doesn't show).
 
Was this at the transformer terminals?
Can you post a better picture of the wiring in the transformer.
Based on the OP nameplate that transformer is not capable of providing a high-leg center tapped output with 120V line to ground.

I have run into more than one person who thought all delta secondaries were center tapped. Industry slang really gets in the way



I was troubleshooting a transformer and found this issue-



It is a step up transformer, 120/208Y to 240v delta - 3-phase. A/C phase used to measure 120 per phase and B was a high leg (130-150).


I measured the voltage Friday and measured 240 across all phases and 240 to ground on A / C phase, but B-phase measured 0 volts to ground. Can you think of any reason why this might be happening?
 

Attachments

  • IMG_1224.jpeg
    IMG_1224.jpeg
    347.4 KB · Views: 8
  • IMG_1221.jpeg
    IMG_1221.jpeg
    18 KB · Views: 8
These are the best pics I have. They are all tapped at the #3 tap which says it’s 100% voltage equaling 240v and 180a. I never measured 120v per phase, which would seam impossible if the total output is 240v.
This transformer feeds a 240v panel. When I was there previously I was told only the one oven had an issue. I received a call today and another oven on a different panel fed by the first panel mentioned had a conductor that had burned up. I had a debate with their handyman saying this transformer and panel were set up to measure 120v per leg and then the high leg was (130-150v).
I’m not a transformer expert, hence the questions.
 
I was told a previous transformer was wired incorrectly and the old panel burned up. This was a while ago.
Should the transformer read 240 total across all phases and 90amps per phase? Or is the transformer label stating those voltages from HV side to the LV side not vice versa
 
When I was there previously I was told only the one oven had an issue. I received a call today and another oven on a different panel fed by the first panel mentioned had a conductor that had burned up.
Open all of the disconnects on the output of the transformer, or disconnect the load wires. Now measure the voltages.

If the voltages are 240 L-L and some equal L-G voltages (roughly 138V) your transformer does not have a problem. It may not be the proper transformer but it is not behaving badly.
 
This is contradictory. Perhaps there used to be a high-leg (different transformer) and at some point it was converted to corner grounded. But a high-leg and a phase 0V to ground should be a dead short, not possible even if the transformer had a center tap for a high-leg (which the label doesn't show).
I think the handyman is referring to the phase that was reading 130-150. When it was installed.
 
Open all of the disconnects on the output of the transformer, or disconnect the load wires. Now measure the voltages.

If the voltages are 240 L-L and some equal L-G voltages (roughly 138V) your transformer does not have a problem. It may not be the proper transformer but it is not behaving badly.
Could there be an issue with the line side that is causing an open delta situation? Which is why I’m reading 0v to ground across one phase
 
Could there be an issue with the line side that is causing an open delta situation? Which is why I’m reading 0v to ground across one phase
Where are you making your measurements.

An open delta will not provide 0V to ground. 0V to ground can only occur if that phase is shortest ground somewhere. On open phase on the wye source windings will not show up as an 'open delta'.

Has the ovens ever worked on this transformer?
Maybe the ovens really do need a center tapped output, and without they have failed.
 
Where are you making your measurements.

An open delta will not provide 0V to ground. 0V to ground can only occur if that phase is shortest ground somewhere. On open phase on the wye source windings will not show up as an 'open delta'.

Has the ovens ever worked on this transformer?
Maybe the ovens really do need a center tapped output, and without they have failed.
I took my readings at the taps on the coil side and at the lugs on the 240 panel. I do not know where the 120v readings were taken from.
Could this delta have been unintentional grounded or a phase bonded to neutral somewhere? As stated earlier a second oven was affected since I was in this shop. This oven is fed by a sub panel from the original 240v panel.
 