I have an existing wastewater treatment plant with a 240/120 volt high leg service.
The process engineer wants to add some packaged blower units. It's basically a blower, VFD, ventilation fan, and controls inside a cabinet
The manufacturers info. indicates their VFD's require a "symmetrical service". They basically want a center grounded wye for the electrical supply. (The also want a ground wire the same size as the phase conductors, but that's not really a problem.)
I'm wondering if I can just add a second transformer supplied from the service transformer, and supply the blowers from the second transformer
The second transformer would be a delta primary to wye secondary transformer, with the center of the wye grounded.
Does anyone see any issues with this plan? The one possible issue i see is that I'm not sure if the existing service is an open or closed delta. (It's supplied with a pad mounted transformer, and I don't think I have ever even seen a high leg service supplied with a padmount before).
If it is an open delta, then I would be closing the delta when I connected to the new transformer. What effect would that have, or is there a way to avoid that?
The process engineer wants to add some packaged blower units. It's basically a blower, VFD, ventilation fan, and controls inside a cabinet
The manufacturers info. indicates their VFD's require a "symmetrical service". They basically want a center grounded wye for the electrical supply. (The also want a ground wire the same size as the phase conductors, but that's not really a problem.)
I'm wondering if I can just add a second transformer supplied from the service transformer, and supply the blowers from the second transformer
The second transformer would be a delta primary to wye secondary transformer, with the center of the wye grounded.
Does anyone see any issues with this plan? The one possible issue i see is that I'm not sure if the existing service is an open or closed delta. (It's supplied with a pad mounted transformer, and I don't think I have ever even seen a high leg service supplied with a padmount before).
If it is an open delta, then I would be closing the delta when I connected to the new transformer. What effect would that have, or is there a way to avoid that?