For the high temp I used the 2% DB temperature from the cooling data. If you want to be more conservative the 1% or 0.4% are good too.So if you use one of the ASHRAE numbers, which is it?
The mean annual low temp (which would have a 50% annual historical chance of exceedance if the data is symmetrical about the mean), or the 5, 10, 20, or 50 year return period lows (with 20%, 10%, 5%, and 2% annual historical chance of exceedance, respectively)?
Cheers, Wayne

For the low temperature I used the Extreme Annual Temperature, Mean, Min DB minus one standard deviation. To be more conservative just subtract more standard deviations and that will reduce the chance that the site experiences a lower temp. But going past 2 SDs is really getting too conservative for me though.