Yes I'm agreeing with you, it's the best solution. Almost zero lead time, and you need a line reactor anyway, so two birds with one stone.You don't replace the service transformer with the DIT, you just mount it next to the VFD, sized only for that drive, just like you would with a Line Reactor. No need to run 4 wires either, you just ground the X0 and leave it that way.
![]()
The DIT is never going to waste enough power to mean squat compared to the costs of a serious upgrade like that.
@steve66
Is this a municipal, or a private sewage plant?