It's trying to prevent the most common sources of cable damage from wallboard fasteners, not all sources. So it has rules on cables through holes in framing members (300.4(A)) and rules on cables installed parallel to framing members (300.4(D)). It does not have any rules on cables running diagonally within a stud bay, or rules on cables within boxes.
So if the additional protection near boxes described in this thread is useful to you because it saves you callbacks or gives you peace of mind, that's great. But this protection is optional, not mandatory.
Cheers, Wayne
It's trying to prevent the most common sources of cable damage from wallboard fasteners, not all sources. So it has rules on cables through holes in framing members (300.4(A)) and rules on cables installed parallel to framing members (300.4(D)). It does not have any rules on cables running diagonally within a stud bay, or rules on cables within boxes.