This MI run below is being converted to EMT w/ RHW 2 hr rated cable. The run is 405' and when I convert pipe and wire I want to make sure I'm accounting correctly for voltage drop. I know I need to determine the actual calculated load which not sure I have enough info. Is there a rating based on below pic I can use for the current for my calc and be safe e.g. the 90A disconnect switch?
Problem is when I put in the parameters into Southwire VD calc I get results below which is larger than the MI cable MI95B cable they designed 3#6. Guess the current at end of cable is important to know and must be less than the 90A I entered???


Problem is when I put in the parameters into Southwire VD calc I get results below which is larger than the MI cable MI95B cable they designed 3#6. Guess the current at end of cable is important to know and must be less than the 90A I entered???