All,
Per the figure, if the 3 hot conductors are straight thru, one raceway to another and the only reason for the box is to pick up a EGC as a wire and not the GRC, is it a "pullbox" per the NEC? I think you are going to say that it is up to the AHJ? To me, if you are not using the box as a "pull point" then it is not a pullbox. The EGC is not spliced, so I don't think it can be considered a "splice box". I'm trying to decide if I need to use the 8x multiplier to size this box for "straight pulls". I get that I'm "down in the weeds", but this forum seems to love this sort of question.
Thanks for any thoughts.
Mark
Per the figure, if the 3 hot conductors are straight thru, one raceway to another and the only reason for the box is to pick up a EGC as a wire and not the GRC, is it a "pullbox" per the NEC? I think you are going to say that it is up to the AHJ? To me, if you are not using the box as a "pull point" then it is not a pullbox. The EGC is not spliced, so I don't think it can be considered a "splice box". I'm trying to decide if I need to use the 8x multiplier to size this box for "straight pulls". I get that I'm "down in the weeds", but this forum seems to love this sort of question.