Designer101
Senior Member
- Location
- California
- Occupation
- Solar and ESS Designer
Fire department wants 200 DEGREES RATED HEAT DETECTOR NOT HEAT ALARM AND COMPATIBLE SMOKE ALARM TO BE IBNTERCONNECTED BY RELAYS
WE USED TO GET KIDDLE HD135 Heat alarm, Kiddle relay (sm 12x) and kiddle smoke alarm (i12060 or i12040A), now the Fire department says they need 200 degrees rated HD.
any body out there has encounted such Equipment. please advice,.
SEE THEIR COMMENTS
1. The plans provided are unacceptable due to the proposed heat ALARM. Heat detectors
should be proposed and should have a higher temperature rating given that the ESS units will be
placed in an unconditioned space. This heat DETECTOR should be as close to 200 degrees as
possible and compatible with the proposed relay, and smoke detectors in the home.
2. Show the interconnection of the proposed heat detector and smoke alarms on the single line
diagram.
WE USED TO GET KIDDLE HD135 Heat alarm, Kiddle relay (sm 12x) and kiddle smoke alarm (i12060 or i12040A), now the Fire department says they need 200 degrees rated HD.
any body out there has encounted such Equipment. please advice,.
SEE THEIR COMMENTS
1. The plans provided are unacceptable due to the proposed heat ALARM. Heat detectors
should be proposed and should have a higher temperature rating given that the ESS units will be
placed in an unconditioned space. This heat DETECTOR should be as close to 200 degrees as
possible and compatible with the proposed relay, and smoke detectors in the home.
2. Show the interconnection of the proposed heat detector and smoke alarms on the single line
diagram.