I'm referencing this mechanical schedule and a bit confused as to what the circuit size needs to be. There are different ampacities listed.

The electrical drawings are calling for one set of #500's in RGS. which is good for 380. Still under any of the ampacities listed below.

Ahhh...I see if I add 125% for continuous load it gets me to 482A. So one set of #500 is not correct.