I'm referencing this mechanical schedule and a bit confused as to what the circuit size needs to be. There are different ampacities listed.

The electrical drawings are calling for one set of #500's in RGS. which is good for 380. Still under any of the ampacities listed below.

Ahhh...I see if I add 125% for continuous load it gets me to 482A. So one set of #500 is not correct.

1771432091942.png
 
Last edited:
We can't see the entire schedule, but with 2 rows, does this chiller need 2 connections, each sized for 482 amps?
 
Looks to me like the electrical engineer was given "800A circuit breaker" as the information to design by, rather than the MCA.

Therefore two sets of 500mcm.
 