zemingduan
- Philadelphia,PA
- Electrical Designer
In a prefabricated manufacture home, the ENT(Electrical Nonmetallic Tubing) is factory installed and is attached to the junction boxes through the connector. The ENT is concealed in wall/ceiling and the junction box is flushed mounted in the wall/ceiling. Only the junction boxes opening are accessible. However, the local fire alarm code amendment requires metal raceway or MC cable for fire alarm wiring. But obvious, only factory installed ENT conduit is provided.
I am thinking to pull MC cable inside the ENT conduit and make sure the conduit fill is met. After all, I think the ENT provide additional protection to the MC cable. I am not sure if local AHJ will allow this. I will verify with the township.
Before verify with local AHJ I want to know if the NEC allow you to pull MC cable inside the ENT if the conduit fill is met? I know this sounds silly because typically you strip off the MC cable metal armor and only pull the conductors inside the raceway when switch from MC cable to conduit. If its' allowed, can I pull the MC cable into the box, strip off the metal armor inside the box, install red head bushing and connect the conductors to the terminals? Or what else do I need?
Thanks!
Thanks!