- Location
- Wisconsin
- Occupation
- PE (Retired) - Power Systems
Other than the requirement for carrying LRA on fire pumps, I can't readily recall any place in the NEC that controls the minimum size of OCPD.
For sure, I regularly used smaller than 125% primary side protection of 75kVA transformers so I could stay in a 100A disconnect.
For sure, I regularly used smaller than 125% primary side protection of 75kVA transformers so I could stay in a 100A disconnect.