Minimum current ampacity

Other than the requirement for carrying LRA on fire pumps, I can't readily recall any place in the NEC that controls the minimum size of OCPD.

For sure, I regularly used smaller than 125% primary side protection of 75kVA transformers so I could stay in a 100A disconnect.
 
Although if it were to pull 23A through a 20A breaker and never ran continuously for several hours at a time, the breaker might never trip.
Actually it could pull 115% forever, per UL listing of minature molded case breakers. OCPD trip curves are based at a specific ambient temperature.
 
Last edited:
now this equipment is in 440- I don’t have my book I am at an event.. it this by default consider continuous use?? For the over current protection device. if it doesn’t state it in 440 this overrides 220.
General rules are chapter 1 through three apply and 400 can modify



90.3 Code Arrangement

This code is divided into the introduction and nine chapters, as shown in Figure 90.3. Chapters 1 through 4 apply generally. Chapters 5 through 8may supplement or modify the requirements in Chapters 1 through 8.
Chapter 9 consists of tables that are applicable as referenced.
Informative annexes are not part of the requirements of this code but are included for informational purposes only.
 
i used to take a continuing education class with an old-school master electrician by the name of fred bender. the guy was the president of the electrical board in the state of nebraska. he was an incredibly well-versed and super-intelligent guy.

one year, he did a motor class and was pretty spot on when someone asked him about what OCPD to install on a motor when we were given the possibility of a 250% on an inverse time breaker. he said, "which one do you install? you install the biggest one you can. why not? do you think the 40a breaker will clear slower than a 25a breaker on a short circuit? nope. do you think the breaker will protect the motor, in the event of overload? NOPE. there's no reason not to put in the biggest one that the code allows."

overlooking the possible price difference, it was hard to disagree with his logic. he was right. the breaker will still function in the event of a short circuit, and protect the insulation on the conductors. and the overload/VFD settings that provide the OL protection are the only things gonna protect the motors, if they go into overload.

the only reason i see not to go to the 25a is just stubborn pride. but, i get it. i've been there too. :)

have a good night.
Makes a lot of sense.
 
Yeah, modify could’ve been the bad term well, like 240 call out that 310.15 circuit size 14 through 10 can be modified based on these sections so they don’t broadly modify it but they do modify it
 
Top