The electrician plan to run the 4#2/0 & #1GND AL SER cable to the 10 x 10 x 6 junction box through the SER cable strap connector and a short section of 1-1/2"C RGC conduit. See the picture below. I think the installation is not code compliance. What do you think?

1. Are you allowed to strip the SER cable and only run the individual insulated conductors after the SER strap connector in the short section of IMC? Do you need a box to transit the SER cable to conduit?
2. 1-1/2" RGC doesn't meet the conduit fill for 4#2/0 & #1GND THHN AL. 1-1/2" IMC does meet the conduit fill though.
3. If he pulls the SER cable in the conduit, the conduit fill shall be met since the RGC conduit is part of the raceway according to the picture in my opinion. The 1-1/2" RGC conduit fill exceed 53% for the SER cable.

1. Are you allowed to strip the SER cable and only run the individual insulated conductors after the SER strap connector in the short section of IMC? Do you need a box to transit the SER cable to conduit?
2. 1-1/2" RGC doesn't meet the conduit fill for 4#2/0 & #1GND THHN AL. 1-1/2" IMC does meet the conduit fill though.
3. If he pulls the SER cable in the conduit, the conduit fill shall be met since the RGC conduit is part of the raceway according to the picture in my opinion. The 1-1/2" RGC conduit fill exceed 53% for the SER cable.