UF (underground feeder cable) 12/4 ?
Its been hard to find UF cable 12/4 , basically 2 hots 2 neutrals with ground. Was having a discussion with another guy that was installing his disconnect with receptacle for the hvac unit at a dwelling. He thought he could use regular romex 12/3.. Its a technicality but romex is not rated for outside as his disco will be outside even though the feed is coming from underneath (crawl space) from the house and feeding the back of the disco.
Also the hvac condenser and receptacle shouldn't be sharing neutrals, even from a 'feeder' (NEC definition vs branch circuit) as this would defeat the purpose of of the receptacle if they needed to shut off the breaker for the diso, (shared neutrals must have common disconnect). Is there a code against this on feeder side?
Cant seem to find 12/4 uf as readily and cheap at the big box stores, do they make it often? What do you think of him wanting to share the neutrals on the 'feeder' side? I couldnt find a NEC code that forbade it, just that its not good practice.
You can enter an exterior disconnect with NM cable that is run in a dry location. Is the crawl space in this installation not a dry location?
yes the crawl space (under house) is a dry location. I always understood it as a 'technicality' , and I believe inspectors here are enforcing it that way as well. The wire connection from the romex is connecting in a wet location (outside in disconnect box) so the romex cannot do that. Is this enforced differently in your area?
The inside of the disconnect is a dry location. Running the cable in a dry location to the dry location inside of the disconnect is permitted. Otherwise every outdoor receptacle or light fixture run with NM cable to an FS box would be a violation.
This is considered to be compliant.
The condenser wouldn't have a neutral connection.
Its 120v unit. Its for a mini split. so it has a neutral.
so share the neutral and put it on a 2-pole breaker. you have to put a disconnect outside at the mini-split condenser anyhow. have that maintenance disconnect only disconnect the condenser 120v lead. the receptacle stays on.
Inspectors classify based on the vapor barrier, some crawlspaces and unfinished basements are damp locations and the vapor barrier is plastic stapled under the floor joists. I would need more info to be sure the crawlspace is a dry location.
He said that in this case it is a dry location so NM is permitted and UF would not be required.
they had a vapor barrier put in some years ago when they put in more insulation, didnt look to great of a job they did with the vapor barrier. some of it moved not 'taped' togheter on the dirt ground. But I guess it still keeping most of the moisture out. Some said they only seen very little.
Interesting some inspectors use the vapor barrier to classify a damp location. What about the existing romex stapled to the studs and no vapor barrier in those places.;-)
I'd be thinking about a 10/3 wg from a 2p 30a breaker to an outside 2 cir 3r Mlo panel with (2) 1p 20's.
One for the GFI receptacle and one for the unit.
But, that's just me.
Jap>
I herd from a HVAC guy you can use a certain kind of Tray Cable in resi now its called Joist-Pull, he supplies it when we wire up a ductless heatpumps nice stuff if I needed 12/4 i'd look into that as I have always liked working with tray cable.
I think it is common to run TC cable from the outdoor unit to the indoor unit. I don't know about the power wires to the condenser. Haven't done a Mini in years. Some generators they use TC cable between the transfer sw. and the gen.