I just saw this thread and I'm scratching my head.
So, the OP thinks he needs 12/2/2 UF. Nowhere does he say directly, but I assume he needs one circuit for the 120V mini-split and another for the 20A service receptacle. Then there's debate over using NM.
Why doesn't he just do two runs of 12/2 UF?? One to the disconnect and the other to the receptacle? He doesn't even need a two pole breaker.
-Hal