Emt as protective sleeve
Pinnie
Ohio
Commercial Electrician
Where does code allow emt as protective sleeve. It’s not in 300.4(b)(1) like I would think. There’s an exception in 300.18 but I’m looking for something more explicit.
Do you mean can EMT be used for the protection or are the cables required to be protected?
I think 300.4(b)(1) requires me to protect low voltage cable through metal studs but the only permitted methods listed are listed grommets/ bushings. I want to use emt.
The better question would be "where does code prohibit emt as a protective sleeve"
The NEC is a permissible code meaning if doesn't say you can't you can. Not everything or method needs to be specifically called out.
You're making the protective sleeve thing difficult when there's no reason. What do you think about using IMC, RMC, FMC, etc....?
I think it should be allowed. I do it all the time. I’m just trying to find the code reference because an apprentice asked me
300.4(b)(1)
“…shall be protected by listed bushing or listed grommets….”
That is for abrasion protection from the sharp edge of the stud it is not for protection for a screw or nail going through the cable. Low voltage cable is not nonmetallic-sheathed cable. NM cable is in Article 334.