I just got a call to price running a feeder from a garage with a 200a panel to a barn to supply a 30a, 120v RV outlet.
There is presently a 20a circuit, but I don't yet know the wire size used. Even #10cu would be iffy with voltage drop.
I would probably recommend #6cu or larger al wire for the distance, and also suggest a 4-wire feeder for future use.
The main question is whether to go with PVC and wires, which would be a bear to pull vs going with direct-bury wire.
Between underground feeder like URD or mobile-home feeder, what are the functional differences between the two?
Thank you as always.