Your math may be fine. But your method is invalid, you can't learn what you need from that.If I did my math right, that’s only 32 amps usage. But that’s just an average over a whole month, right? So it could be days using a lot more than that obviously, we had a cold spell in February, I believe here..
I'd give it a 2% chance that you need more than 200A.I’m thinking on going head with a 400 service, enlarging the 2 inch riser to 2 1/2 inch and enlarging the 4/0 to 350.
Do the load calc per the optional method,. get the utility data, get the CT meter described above.
Only a tiny fraction of homes need 400A after you do the numbers right.