Are you sizing these at a continuous load rating? Is that necessary considering the wire is undergoing derating and ampacity adjustments?Not sure what your actual load is but for the minimum conductor size I ran these through the Southwire VD calculator and got these numbers for:
120 volts, 350', 3% VD, Copper conductors, (Aluminum conductors):
30 amps-#1/0 (#3/0)
25 amps-#1 AWG (#2/0)
20 amps-#2 AWG (#1/0)
15 amps-#4 AWG (#2 AWG)
10 amps #6 AWG (#3 AWG)