250.104 Bonding of Piping Systems and Exposed Structural Steel.
(A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with
250.64(A), (B), and (E).
The points of attachment of the bonding jumper(s) shall be accessible.
(1) General. Metal water piping system(s) installed in or attached to a building or structure
shall be bonded (1) to the service equipment enclosure, (2) the grounded conductor at the service, (3) the grounding electrode conductor where of sufficient size, or (4) to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with
Table 250.66 except as permitted in
250.104(A)(2) and
 (A)(3).
No matter what one would think it meant there are only four places any metal water pipe can be bonded and I don’t see to another water pipe listed. (1), (2), (3), and (4) was added by me to making counting those places easier.
Here is what the Code Making Panel had to say in 2008;
5-235 Log #1834 NEC-P05
Final Action: Reject
(250.104(A)(1))
____________________________________________________________
Submitter: Mark T. Rochon, Mark J. Rochon Master Electrician
Recommendation: Revise as follows:
General Combination metal water piping system(s) separated by nonmetallic  water piping system(s) where may become energized installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used.
Substantiation: Nonmetallic water piping systems are being inserted between our metal water piping system and today’s code is not recognizing these changes.
Panel Meeting Action: Reject
Panel Statement: The conditions indicated in the substantiation are already covered by 250.104(B) where there is not a complete metallic water piping system.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15