mtnelect said:
Grounding has become less important since the introduction of plastic water pipes in new construction. Most of the water companies routinely install plastic pipes from their water mains to the water meters. So there has been less emphasis on grounding. What is there to ground ?
Michael, IMO, this statement reflects the disorder of Article 250 - nothing has changed, as far as "what's left to ground?" The electrical service is required to be grounded (earthed), and nothing has changed by a shift in what electrodes are available or common in structures. It's still required to be earthed as much today as yesterday.
All the references I saw in the article you linked to over at IAEI (which admittedly, I only skimmed halfway through) were related to getting the service connected to earth.
The critical change that comes about by the shift to more non-conductive piping being used for water piping is that there's "nothing left to bond." Bonding is different, in that the service couldn't care less about the water piping, it receives no benefit from the connection - the bonding is solely for the operation of OCPDs in the event that the water piping becomes accidentally energized.
This can be a valuable, lifesaving connection - but the text in 250.104(A) is so poor that it's really hard to determine just how far we must go in the name of bonding water pipes. There have been some pretty good discussions about this here in the past, you might have seen them.
I don't understand why your responses keep centering around the IAEI site. I don't care what they know or have, to be brutally honest.
I
do care about the people that come here (because this is where I am) and that may benefit from a discussion about this, that, or the other. If you (or Quoque) still feel that grounding electrodes are to compensate for open neutrals, by all means, speak up and let's discuss it - don't be bashful.