Re: 1? / 3? Neutral Amp Question
That's the equation I was looking for yesterday. I think we should stick with Wye configurations for this discussion.
When we use the equation for L-N loads, we are putting in phase currents. So if we put in 50A for A, and 50A for B, those two currents are assumed to be 120 deg apart (they have to be for the equation to work).
That is a completely different case than having a L-L load. In this case the 50A is not in phase with either of the currents in the above situation.
Steve
That's the equation I was looking for yesterday. I think we should stick with Wye configurations for this discussion.
When we use the equation for L-N loads, we are putting in phase currents. So if we put in 50A for A, and 50A for B, those two currents are assumed to be 120 deg apart (they have to be for the equation to work).
That is a completely different case than having a L-L load. In this case the 50A is not in phase with either of the currents in the above situation.
You could do that knowing that L-L loads don't contribute any neutral current. Or you could convert your L-L loads into phase currents.So in figuring the neutral current, you'd first have to eliminate all line-line loads from the phase totals, and then proceed with the calculation?
Steve