1.5 or 2" emt / 41 # 10 thhn wires in a conduit

Status
Not open for further replies.

arnettda

Senior Member
I am installing 41 # 10 thhn wires in a conduit. 20am ckt. Using #10 because of derating. 50 % from 310-15b2. This is for a lighting dimmer. All ckts have there own neutral. I do not believe I need to count the neutrals. 310-b4. Am I right? Also Table C-1 says I can put 63 # 10's in a 2inch emt. Would you use 2" or bump it up to 2.5"? I have never installed this many wire in a conduit. and would like to know if the extra room would make life easier. Thanks.
 

Rewire

Senior Member
If each circuit has its own neutral then it can only carry full current and must be counted,if I read your post correctly you are not using MWBC so you are not sharing a neutral.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Hopefully your 41st wire is an equipment ground.
As stated above, if you have a seperate neutral per circuit, it counts in your derating, howver, 40 #10 would result of 40% of 40 amp rating or 16 amps. I would think if your loads don't exceed 16 amps you are still good to go.
 

arnettda

Senior Member
Hopefully your 41st wire is an equipment ground.
As stated above, if you have a seperate neutral per circuit, it counts in your derating, howver, 40 #10 would result of 40% of 40 amp rating or 16 amps. I would think if your loads don't exceed 16 amps you are still good to go.

Yes it is an equipment ground. And the derated value just applies to the amount of load you can apply to it? Also would you use the 1.5 or 2" Thanks to all who have replied.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So you have 40 CCC's and an EGC? Is that why your derated value is 16 amps? (40a*40%=16a).

Personally I would use more than one conduit.
 

Smart $

Esteemed Member
Location
Ohio
Hopefully your 41st wire is an equipment ground.
As stated above, if you have a seperate neutral per circuit, it counts in your derating, howver, 40 #10 would result of 40% of 40 amp rating or 16 amps. I would think if your loads don't exceed 16 amps you are still good to go.
Load doesn't matter... derating is about circuit ampacity. He'd have to put all the circuits on 15A breakers...
 

arnettda

Senior Member
So you have 40 CCC's and an EGC? Is that why your derated value is 16 amps? (40a*40%=16a).

Personally I would use more than one conduit.

I have 120 ckts total. Abut 60 feet between locations. 2 seperate floors. Will have 6 conduits all together. Or would I be better going with even more conduits.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have 120 ckts total. Abut 60 feet between locations. 2 seperate floors. Will have 6 conduits all together. Or would I be better going with even more conduits.


Personally, for ease of pulling I would use only 1" conduit and fill accordingly. You could still do it your way and install 40 CCC's, in one conduit, with an adjusted ampacity of 16 amps and protect them at 20 amps.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Given that the runs are kind of short I might consider running 1.25" EMT but as aforementioned I would forgo using any larger conduit to make pulling easier.
 

Smart $

Esteemed Member
Location
Ohio
...with an adjusted ampacity of 16 amps and protect them at 20 amps.

Provided the condition of 240.4(B)(1) is met for all 20 circuits?which is to say they "...are not part of a multi-outlet branch circuit supplying receptacles for cord-and-plug connected portable loads." Otherwise they will have to be protected at 15A.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you derate to 16amps would you need a 15 amp instead?


Since these are not multi-receptacle circuits and 16 amps is not a standard size, 240.4(B) would permit the next standard size OCPD which is 20 amps.
 