I am installing 41 # 10 thhn wires in a conduit. 20am ckt. Using #10 because of derating. 50 % from 310-15b2. This is for a lighting dimmer. All ckts have there own neutral. I do not believe I need to count the neutrals. 310-b4. Am I right? Also Table C-1 says I can put 63 # 10's in a 2inch emt. Would you use 2" or bump it up to 2.5"? I have never installed this many wire in a conduit. and would like to know if the extra room would make life easier. Thanks.