1.5 or 2" emt / 41 # 10 thhn wires in a conduit

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
That may or may not be true. In the theater project I'm currently involved with it's not true. But I agree that it's a poor design and would opt for more conduits with less CCC's. That was one of the reasons that I said that the conduit I would use would be 1" or 1.25".

All I am saying is it could go either way. If each circuit is supplying a fixed load I don't see a problem, if each circuit supplies lighting receptacles for changing lighting equipment I would want to wire for worst case loading.

I agree with you, more conduits of smaller sizes. :smile:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
All I am saying is it could go either way. If each circuit is supplying a fixed load I don't see a problem, if each circuit supplies lighting receptacles for changing lighting equipment I would want to wire for worst case loading.

I agree with you, more conduits of smaller sizes. :smile:

You're 100% correct. In some installations dimmer racks do serve receptacles.
 