Rewire
Senior Member
- Location
- Lake of the Ozarks
Since these are not multi-receptacle circuits and 16 amps is not a standard size, 240.4(B) would permit the next standard size OCPD which is 20 amps.
I realized that after I posted
Since these are not multi-receptacle circuits and 16 amps is not a standard size, 240.4(B) would permit the next standard size OCPD which is 20 amps.
Since these are not multi-receptacle circuits...
I must have missed that somewhere
I assumed since he said lighting dimmer......
That was my assumption too. :wink:
I am installing 41 # 10 thhn wires in a conduit. 20am ckt. Using #10 because of derating. 50 % from 310-15b2. This is for a lighting dimmer. All ckts have there own neutral. I do not believe I need to count the neutrals. 310-b4. Am I right? Also Table C-1 says I can put 63 # 10's in a 2inch emt. Would you use 2" or bump it up to 2.5"? I have never installed this many wire in a conduit. and would like to know if the extra room would make life easier. Thanks.
Individual neutrals is spec.why cant you set a gutter on top of the conduits and install neutral and ground bars, then bring up just one big neutral and EGC then all the individual neutrals/EGC's never leave the gutter. that also would cut down on heat because there would be very little actual current on the neutral
Individual neutrals is spec.
Hey anybody have that pic of the yellow Romex wallpaper job to show the OP as an alternate way to install that many circuits?
Still picking my chin up off the floor. I've wallpapered with pipe before but never romex. That's awesome.one of these?
I find it hard to believe 40 circuits are all going from point "A" to point "B" and there couldn't be an advantage to running say 4 cc pairs in 3/4" C , in different directions, and protecting w/ 20A bkr.
Since the loads are dimmers (non-linear) I expect the wires are going to heat up and you would benefit from the conservative approach.
There are 120 ckts total. I will not be running 40 ckts in one pipe anymore. It will be more like 10.
Paul Bunyan, move over!Pfff...I could push 40 circuits down that pipe. No soap just a little spit. You should write a story about me some time.
There are 120 ckts total. I will not be running 40 ckts in one pipe anymore. It will be more like 10.
Since these are not multi-receptacle circuits and 16 amps is not a standard size, 240.4(B) would permit the next standard size OCPD which is 20 amps.
Often dimmer racks do supply multi receptacle circuits and they often get loaded up.
Protecting 16 amp conductors at 20 amps is a bad design for this IMO.