Quite a bit actually. Nothing rare about the transformer at all.Not true. The 2014 Handbook has explicit author's commentary following 240.4(F) that explicitly refers to these circumstances as "special cases."
Am I taking a little bit of creative freedom in going from "special case" to "rare exception?" Yes, but that is hardly a stretch.
Not at all. It's just that most loads use 120/240 nowadays instead of straight 120 or straight 240.Both phrases imply a degree of rarity.. and I maintain that the ability to wire any dual winding, multiple voltage output xfmr as a "2-wire (single voltage) secondary" (even if listed on the nameplate) is a direct contradiction to said rarity.
You are way off base. Don't be so set that two terminals outside the tank means only one winding. You may pop the lid and find that the windings are jumpered internally and you still have two windings giving you a two-wire output the same as if you had three or four terminals outside the tank to look at and ponder over
It means nothing.