paul32 said:I would think this is relatively common to have an air conditioner with max breaker of 35 or 40A and the MCA under 30A, which would only need 10AWG wire. The square D breakers 35A and up aren't rated for wire smaller than 8AWG. So what do you do?
John Valdes said:I would use the correct wire size for the breaker. 30 amp gets #10 for the complete run. 35 amp gets #8.
celtic said:WTF?
![]()
paul said:My thoughts exactly when I noticed that you use Netscape Navigator. :-?
guschash said:I use the correct wire size for the breaker. I size #10 with 30amp breaker. When I was a industial electrician, we told to always protect the machinery. So we never fuse higher than what the motor called for and never use smaller wire.
guschash said:I use the correct wire size for the breaker. I size #10 with 30amp breaker.
iwire said:There are many 'correct' size wires for 30 amp breakers.
There are times that it is perfectly acceptable to use 14 AWG with a 30 amp breaker.