I have 10 lights pulling 1.5 amps each. 15 amps total what size circuit breaker is required. do you multiply 125% which would be a 20 amp breaker.
Are the lights going to be on continuously for three or more hours?I have 10 lights pulling 1.5 amps each. 15 amps total what size circuit breaker is required. do you multiply 125% which would be a 20 amp breaker.
Are the lights going to be on continuously for three or more hours?
15A breaker then.
Wouldn't the question be if 9 or more of the lights are going to be on continuously for three or more hours?Are the lights going to be on continuously for three or more hours?
Yes. But the heart of the question is can you run 15A of load on a 15A circuit. At least that's the way I read it.Wouldn't the question be if all the lights are going to be on continuously for three or more hours?
Of course, but it's Friday afternoon...Yes. But the heart of the question is can you run 15A of load on a 15A circuit. At least that's the way I read it.
Getting all giddy thinkin' about the weekend, are ya?Of course, but it's Friday afternoon...
Getting all giddy thinkin' about the weekend, are ya?
Covered in post #2.If the lights are going to be on for 3 hours or more, take the total amps and multiply it by 1.25. So 15 x 1.25 = 18.75 amps. Which in this case, under a continuous load (lights are on 3 hours or more) you will need a 20 amp breaker.
If your lights are not going to be on for 3 hours or more, take the total amps of the lighting load which is 15 amps. Then go to the code book under 240.6 and find the breaker size that is closest to 15 amps but not under 15. In this case, you have a overcurrent protection device (breaker) that is exactly 15 amps. So that is your answer, 15 amp breaker.
I thouhght all lighting loads were consider contionuous
Covered in post #2.
My bad, basically just wanted to share the code reference though. So people know exactly what breaker (OCPD) to buy.
No worries, welcome to the forum.
What code section would you say applies in this case?
Only loads that are expected to run at maximum for three hours or more OR loads the NEC specifically tells uss to treat as continuos loads must be considered continiuos.
See article 100 for defintion of continiuos load.
We are always free to choose to treat any load as continuos if we want.
Thanks, really enjoying the forum! Going to turn me into a badass electrician haha
Code reference would be:
Article 240: Overcurrent Protection.
240.6(A) is for Standard Amp Ratings for fuses and Circuit Breakers.
210.20(A) Continuous and Noncontinuous Loads. Lets you know when to multiply by 1.25 (125%) of the load.