Or it could be that I am in a position to make others do it while I type on a keyboard.
:thumbsup:
Or it could be that I am in a position to make others do it while I type on a keyboard.
It meets the job specs and have never found it to be a hardship to use.
Just curious do they make a 4\0 in solid. The spec calls for #10 and Larger to be solid. Hmmm is that a loophole around the spec for the contractor?
Charlie, look at any of the conduit or tubing article 3xx.26 sections
Roger
IMO #10 solid in raceways should be banned. With modern value engineering conduits are being filled to their absolute maximum. #10 solid only makes it more difficult to install with no real gained value to the end user.
In my opinion the additional labor costs exceed the cost increase between solid and standed. There is no way that it pulls as quick and as easy as stranded.It meets the job specs and have never found it to be a hardship to use.
How is solid better in wet locations?My personal opinion is that solid is much better in wet locations. In dry locations the only advantage to me is ease of termination.
I keep forgetting about the cable stuff....don't see much if it around here.I am just so used to working with solid MC in 10 AWG I don't find 10 THHN hard to work with.
Unless it is in walker duct, then it is awful. :rant:
How is solid better in wet locations?
Or it could be that I am in a position to make others do it while I type on a keyboard.
I would not be, I spent last night working pulling long cable runs across a store ceiling.
In my opinion the additional labor costs exceed the cost increase between solid and standed. There is no way that it pulls as quick and as easy as stranded.
I guess part of it would be that I have rarely done anything other than industrial work in past 20 years and we don't use any solid other than CAT5e on our industrial jobs.
I wondered that myself.How is solid better in wet locations?
That means you have a hole in the insulation. Hopefully the ends are not submerged or you are looking for more troubles at some point anyhow.Probably because water can more easily wick into the stranding.
Besides the bare ground #4, the largest manufactured solid is #10. I have seen #8 solid for older installations but i don't think it is manufactured anymore.
I have used #2 SBTC for ground. SBTC = Solid Bare Tinned Copper.
And it's no fun to work with.
#10 and larger? Are you sure he didn't mean #10 and higher (smaller)? I wouldn't want to be pulling 4/0 solid wire.I have a contractor asking me for an exception to a specification requirement that says #10 and larger shall be solid. They want to use stranded #10 for a specific application. I have no basic objection, but I would like a sanity check on their reason for the request. They stated, "10AWG can be pulled through RMC only on a straight line. We require 10AWG for the Water Heater line with multiple 90 degree bends in the RMC conduit."
Does anyone have an opinion on the statement that "10AWG can be pulled through RMC only on a straight line"?
Looking at materials on POCO trucks sometimes there are some rather large solid conductors - always bare conductors.
It still has to get under the insulation and that would be the same for either. Water between the stands without insulation damage is not an issue unless it is running out of the conductor onto the energized parts.Probably because water can more easily wick into the stranding.
It still has to get under the insulation and that would be the same for either. Water between the stands without insulation damage is not an issue unless it is running out of the conductor onto the energized parts.
If the water is getting into the conductor as a result of insulation damage, I would agree that the stranded conductor would fail quicker, but they would both fail.I am going to say you are mistaken in that.
I have a lot of first hand experience with this and with smaller stranded conductors water wicked into the stranded destroys the wire much faster than a solid conductor.