jxofaltrds
Inspector Mike®
- Location
- Mike P. Columbus Ohio
- Occupation
- ESI, PI, RBO
Like was said above....we (POCO) will not connect a 100A service to a 200A panel even if it has a 100A main. For the obvious reason that if the customer pays fees for a 100A service, then as soon as we leave goes back and replaces the main to 200A, he gets a nice discount. Also, if the service drop is sized for 100A, the wire may not be able to handle 200A worth of load. Changing a main hot is a BAD idea, since the service is unprotected except for the transformer fuse when you are ahead of the main. Also, as stated above, pulling the meter means cutting the seal. Another bad idea. Many utilities always size service drops for 200A and charge fees based on 200A or less. But not all. Not idiots, but not very trusting either. You know the old saying...."Trust but verify".
Please inform the POCO that if you have a 100 main then your panelboard is 100 amps and meets:
408.36 Overcurrent Protection. In addition to the requirement
of 408.30, a panelboard shall be protected by an
overcurrent protective device having a rating not greater
than that of the panelboard. This overcurrent protective device
shall be located within or at any point on the supply
side of the panelboard.
It says "NOT GREATER".
If you want you could back feed as I stated earlier:
408.36
(D) Back-Fed Devices. Plug-in-type overcurrent protection
devices or plug-in type main lug assemblies that are
backfed and used to terminate field-installed ungrounded
supply conductors shall be secured in place by an additional
fastener that requires other than a pull to release the
device from the mounting means on the panel.
Panelboard. A single panel or group of panel units designed
for assembly in the form of a single panel, including
buses and automatic overcurrent devices, and equipped
with or without switches for the control of light, heat, or
power circuits; designed to be placed in a cabinet or cutout
box placed in or against a wall, partition, or other support;
and accessible only from the front.
IMHO you can use whatever cabinet you choose.
Cabinet. An enclosure that is designed for either surface
mounting or flush mounting and is provided with a frame,
mat, or trim in which a swinging door or doors are or can
be hung.