Sounds like he will be utilizing feeder taps and not have to tap service conductors.Are you working under the 2020 NEC? If so, are you having to deal with 230.46?
Sounds like he will be utilizing feeder taps and not have to tap service conductors.Are you working under the 2020 NEC? If so, are you having to deal with 230.46?
I never understood that reasoningthe poco kw rate for single phase was much cheaper.
The warehouse down the road that he bought later had an open delta three phase service. He had it changed to single phase too, to get the cheaper rate. It was previously a sewing plant, but all he needed was lights.I never understood that reasoning
energy charge shouldn't really change, I can see different base charges depending on equipment needed to deliver the service. But at same time how much does it cost them to have a 75 kVA single phase pot on a pole vs three 25's? The 25's are probably one the most common pots they keep in the warehouse as well.I never understood that reasoning
A lot of discussion has strayed away from that.The power company only has 120/240 single phase to that area
So power company now says 1000amp single phase is to hard to get a transformer for. Has anyone had any work with 120/240 3 phase?
As the OP said in #1-
A lot of discussion has strayed away from that.
Both you were replying to the person that posted the OP.The op asked about delta in post #17: