Don't you need at least a 100A service to a separate structure?
AFAIK, 100 amps 3 wire service is the minimum permitted for a home.
Much smaller services are permitted for non residential structures.
Don't you need at least a 100A service to a separate structure?
I'm need to power a small shed on a golf course with 20 amps at 240 volts.
the closest source is a 1000 feet away. What size wire would handle my
voltage drop conserns.
AFAIK, 100 amps 3 wire service is the minimum permitted for a home.
Much smaller services are permitted for non residential structures.
Took a better look at this project, turns out I'm looking at a 850' run. My source is a 277/480 panel that has to feed a 20'x30' club house. With (2) lighting circuits and (2) receptacle circuits. I'm thinking 3 #2 conductors 120 volts.
I would be willing to bet that AC and heat will soon be added, even if only 120v units.Took a better look at this project, turns out I'm looking at ... a 20'x30' club house. With (2) lighting circuits and (2) receptacle circuits.