Anybody have any suggestion where to get info on 105 degree C, 600V, 2/0 conductors?
Are you sure its 600 volt? 105C is generally associated with higher voltage conductor.
Internal WH wiring for 4500 W elements is normally #12 and rated for 105? C.![]()
Anybody have any suggestion where to get info on 105 degree C, 600V, 2/0 conductors?
Anybody have any suggestion where to get info on 105 degree C, 600V, 2/0 conductors?
How would that be a code problem using a higher voltage rating than what is required? Kinda like using a # 10 AWG on a 20-amp circuit.Are you sure its 600 volt? 105C is generally associated with higher voltage conductor.
How would that be a code problem using a higher voltage rating than what is required?
wiring is for an electric humidifier. Manuf specifies 105 degree rated insulation for feeders.
don't think i can use AWM since that wiring would be listed for appliances.
If it is a Branch Panel circuit or any kind of feeder circuit there is no requirement for it to be 105 C wiring in the NEC I know of. Doesn't mean you cannot use it if you want to spend that kind of money, but there is no justification or safety reason you need to use it. There are no terminations made for 105 C.don't think i can use AWM since that wiring would be listed for appliances.
This is the first thing I noticed.
And also, if you're involved in equipment that has these kind of requirements, Shouldn't you already know of this stuff.
I apologize for being rather unsympathetic, and I do actually mean that, but what you're asking about you should already know.
That is what I was thinking and why I asked leading questions. If it is for the feeders, heat is a function of current, cable size, raceway, and number of current carrying conductors. You could use 105 C wire for derating calculation purposes, but still the terminal equipment is not rated for 105C terminations. Is it a high heat enviroment or something like a boiler room or furnace?It sounds like maybe this wiring is for the equipment itself where internally heat is an issue.
. no need to apologize for being unsympathetic but you could work on your arrogance.
Did it say "feeders"?. . . While reviewing the manufs specification it said to use 105 degree rated insulation for the feeders . . .
. . . I know there is no code requirement for the feeders to be 105 degree C but because it is part of the manufs specs it needs to be followed.