stickboy1375 said:I like to think my work is top notch , but dont think I'm drilling 1 hole per wire.. or 3 or 4 for that matter:grin:
But why would anyone want to drill 3 or 4 holes for one wire?:grin:
stickboy1375 said:I like to think my work is top notch , but dont think I'm drilling 1 hole per wire.. or 3 or 4 for that matter:grin:
codedude said:E3605.4.4 ? where more than two NM cables containing two or more current carrying conductors pass thru wood framing that is to be fire or draft stopped , the ampacity of these conductors must now be adjusted per table E3605.3
This "new" code section in the 2006 IRC would limit the # of wires passing thru a hole unless the ampacity was adjusted and figured into the installation. This is something inspectors do not generally do in the field so it might be safe to say there is a limit on how many wires can pass thru certain holes. At least thats the way I see it.
Only two cables passing thru one hole is O.K., It was found that with more than two cables there is a potential for excessive build up of heat.
This would apply to electrical penetrations thru fire blocks, draft stops, and thru top plates. (code commentary)
dlhoule said:But why would anyone want to drill 3 or 4 holes for one wire?:grin:![]()
srblx said:I agree with Nemo that last hole has Cat5 in it. Does that not violate code as running within 6 inches of a branch circuit or is it now 12 inches of separation for lv and power wires?
lpelectric said:I've never heard of 6" or 12". This would be very hard to accomplish. :smile:
raider1 said:It amazes me at how many electricians ask me what it is I want to see.
I tell them its not what I want, but what the code requires.
Chris
bhsrnd said:I believe you'll find this in EIA-569. EMI sources (lighting, electrical wiring, etc.) can wreak havoc on LAN cabling and data transmission. I've personally seen LAN cabling draped across fluorescent lighting cause anomalies on a user's network connectivity and once the cable was relocated all problems stopped.
True CAT6 networks are even more susceptible to interference because of their high data transmission rates. "True" meaning not just CAT6 cable but CAT6 switches, routers, etc..
lpelectric said:Thanks for the info. I didn't set out to learn anything today, but you got me! :smile:
bhsrnd said:I believe you'll find this in EIA-569. EMI sources (lighting, electrical wiring, etc.) can wreak havoc on LAN cabling and data transmission. I've personally seen LAN cabling draped across fluorescent lighting cause anomalies on a user's network connectivity and once the cable was relocated all problems stopped.
True CAT6 networks are even more susceptible to interference because of their high data transmission rates. "True" meaning not just CAT6 cable but CAT6 switches, routers, etc..
The separation is for conductors, not cables. If you accept that Cat 5 cable can be run in the same bored hole as rigid conduit, then its allowed for NM cable, as both are chapter 3 wiring methods.lpelectric said:Not sure if this applies, but look at Art. 800.133(A)(2) which requires 2" separation. I've never heard of 6" or 12". This would be very hard to accomplish. :smile:
stew said:i dont think derating is a problem . you must have 24 inches or more of bundling before you have to derate right?
augie47 said:stew, if I'm not mistaken the way 2008 334.80 is worded, the 24" rule will not apply with romex cables thru holes that are "filled"(caulked, etc)