Drop me a PM when you get close. I'll hook you up with some good food and some class accommodations.
Agreed... I was just wondering if there was any wiring advantage to either switch first or box first as far as conductor fill or cable runs.
We also need to mention there is exceptions that don't require the grounded conductor to be there if it is a raceway wiring method or is constructed in a way that it allows easy access to later install the grounded conductor should it be needed.To answer your question, there are devices such as occupancy sensors, dimmers, etc that require stand-by power which needs a neutral. In the past these just used the EGC for the neutral power. They draw very little power and the thought was it was ok to use the EGC for the neutral. Now (2011 and later) a real grounded/neutral is required for these devices. This is to keep unwanted current off the EGC and any metallic paths.
Edit: Even though a standard SP switch is installed, the thinking is one of the devices may be installed later and they want the neutral to be there if needed.
Francisco's was always a good choiceDrop me a PM when you get close. I'll hook you up with some good food and some class accommodations.
We also need to mention there is exceptions that don't require the grounded conductor to be there if it is a raceway wiring method or is constructed in a way that it allows easy access to later install the grounded conductor should it be needed.
This also only applies to lighting loads supplied by a general purpose branch circuit that utilizes a grounded conductor, in general that means it only applies to switches for 120 volt lighting or 277 volt lighting, but there could be other somewhat unusual circumstances where it would apply.
Still is. Haven't been in a while though.Francisco's was always a good choice
It is important to note that it was the designers/manufacturers of the occupancy sensors and other "powered" switching devices and the UL standard that was putting the current on the EGC.To answer your question, there are devices such as occupancy sensors, dimmers, etc that require stand-by power which needs a neutral. In the past these just used the EGC for the neutral power. They draw very little power and the thought was it was ok to use the EGC for the neutral. Now (2011 and later) a real grounded/neutral is required for these devices. This is to keep unwanted current off the EGC and any metallic paths.
Edit: Even though a standard SP switch is installed, the thinking is one of the devices may be installed later and they want the neutral to be there if needed.
It is important to note that it was the designers/manufacturers of the occupancy sensors and other "powered" switching devices and the UL standard that was putting the current on the EGC.
This rule was not triggered by electricians trying to use the EGC as a grounded conductor.
I thought the rule change was just so we would have something to complain about on internet forumsYep, I didn't get into all that when I posted to try and answer the question and keep it short and to the point.
I do know that the rule was just a concession between the NEC and UL, and not the electricians that were the reason for the code.
Sometimes also called a California three way or a Chicago three way, or maybe a few other names but those are both common names for a set up where you supply two three way switches with both circuit conductors (connected to the "traveler" terminals and then bring the "common" terminal from each switch to the controlled load. Biggest problem with using this arrangement with an Edison base lamp is that it reverses polarity to the load to control it, and this leaves the shell of the lampholder being connected to the ungrounded conductor depending on the switch positions which is the code violation that primarily prohibits using this method.Never heard the term California Travelers
California travellers just means you use 12-2 or 14-2 romex for your travellers in a three way switch. It's code legal. The old Carter or Chicago three way is not the same thing.Sometimes also called a California three way or a Chicago three way, or maybe a few other names but those are both common names for a set up where you supply two three way switches with both circuit conductors (connected to the "traveler" terminals and then bring the "common" terminal from each switch to the controlled load. Biggest problem with using this arrangement with an Edison base lamp is that it reverses polarity to the load to control it, and this leaves the shell of the lampholder being connected to the ungrounded conductor depending on the switch positions which is the code violation that primarily prohibits using this method.
California travellers just means you use 12-2 or 14-2 romex for your travellers in a three way switch. It's code legal. The old Carter or Chicago three way is not the same thing.
As far as I know California Travelers are only standard practice in California. There are a few Californicators that try to bring this style of wiring into my state; they are dealt with on a case by case basis.